Primary control based on network security (PCNB) is among the system-supporting capabilities for power-generating units, storage, and continuously controllable loads. This represents the national implementation of LFSM-O/U operation, as required by the Connection Code Requirements for Generators (RfG). Primary control based on network security replaces the traditional “operation along the characteristic curve” in over- and under-frequency ranges.
As the name suggests, primary control based on network security (PCNB) is a form of primary frequency control that activates when the frequency deviates beyond the band of 50 Hz ± 200 mHz, with the goal of regulating the frequency gradient to zero. It differs significantly from the previously established P(f) control in the Technical Connection Rules (TCR), which followed a predefined characteristic curve. In contrast, primary control based on network security aligns the active power control rates of generation units with a defined inertia. For conventional power plants and grid-forming converter-based units, this is inherent inertia.
However, grid-following converter-based units do not possess their own inertia. They rely on the system’s inertia, i.e. of other grid-forming units, which the primary control based on network security coordinated to ensure stable operation.
When considering the closed control loop formed by frequency-power control and system inertia, a correctly designed system remains stable under both small-signal and large-signal disturbances. In this configuration, the unit exhibits self-stability with respect to frequency and active power behavior. This means the unit can autonomously stabilize itself during certain disturbances within its voltage and frequency limits. The collective behavior of such self-stable systems is also stable, forming a crucial foundation for managing major disturbance events, such as a system split.
If a grid-forming unit with substantial real or virtual inertia only requires a small portion of it for its own stability due to its fast control capabilities, it can then share the remaining portion of its inertia available with the grid-following units in the system, enabling their stable operation.
Frequency-controlled disconnection and reconnection of loads
Another system-supporting capability is the frequency-controlled switching of consumer installations such as heat pumps and unidirectional charging devices for electric vehicles. If primary reserves and primary control based on network security cannot restore the balance between generation and load quickly enough, the mains frequency may drop excessively and fall outside the defined operating limits.
In the event of a load shortfall, the frequency may fall below the threshold of 49.0 Hz. In such cases, the automatic under-frequency load shedding (UFLS) has traditionally been used as a last resort in the system protection plan. This involves disconnecting one or more supply areas at the distribution network level, significantly reducing power consumption.
However, due to the high penetration of renewable energy (RE) systems in the distribution grid, these RE systems would also be disconnected during UFLS events, resulting in the loss of their valuable capabilities for supporting the system during disturbances and restoring normal operation.
Therefore, selective and non-discriminatory load shedding will no longer be feasible in all network usage scenarios via UFLS. Nevertheless, UFLS remains an essential measure within the system protection plan.
Its effectiveness should be preserved through the implementation of frequency-controlled switching in the Technical Connection Rules for non-continuously controllable consumer installations (e.g., heat pumps and charging devices), as these will have a significant impact on system stability in the future.
Where are these requirements specified?
Low voltage | Medium voltage | High voltage | Extra high voltage |
- Minimum requirements in the TCR for generation in LV, expected from 2027 onwards
| - Minimum requirements in the TCR MV, expected from 2027 onwards
| - Minimum requirements in the TCR HV, expected from 2027 onwards
| - Minimum requirements in the TCR EHV, expected from 2027 onwards
|